OT - Electric Service in Garage

I wanted to upgrade my electric service in my detached garage from an extension cord to a 30Amp 240V panel. I don't run too much in my garage. Just a compressor and other power tools.

I know some people have heavy duty garages on this board. Mine is a 1 car detached about 50' from my house. I wanted to run plastic conduit with 10/3 UG feed wire.

Is 30A too much? How many circuits can I run off this panel? Before I consult a pro, I thought I'd try here.
westville is offline  
Sponsored Links
Advertisement
 
post #2 of (permalink) Old 05-09-2005, 03:10 PM
Keyboard Implanted
 
lomodyj's Avatar
 
Join Date: Jan 2002
Location: Chapel Hill, NC
Posts: 3,761
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

Is your garage gonna be at the Bash? if so we could likely work on it there.

Really, 30 amps should do for a small compressor and some lights or power tools, but don't try to run a bunch of stuff at the same time. You will want to run 8 guage wire (minimum) for that long of a run.
lomodyj is offline  
post #3 of (permalink) Old 05-09-2005, 03:38 PM
**DONOTDELETE**
Guest
 
Posts: n/a
Re: OT - Electric Service in Garage

If you are running 30A 240vac, then in reality you will have two 30A 110Vac circuits...which is plenty of juice for most things....assuming your not running something off 240.
At the house, you will need a dual 30A breaker...Lom is right about the wire size.
You might want to check building codes...If you plan to seel later and leave the wiring, you will have issues.
You want to run the wires to a couple of breakers in the garage and then branch off from there.
Sponsored Links
Advertisement
 
post #4 of (permalink) Old 05-09-2005, 06:30 PM
 
Join Date: Sep 1999
Posts: 1,741
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

cant run a welder off 30amps, need 50 amps.
Brownbagg is offline  
post #5 of (permalink) Old 05-09-2005, 06:38 PM
Moderator
 
Jim_Lou's Avatar
 
Join Date: Dec 2001
Location: Belleville, Illinois
Posts: 11,487
Thanks: 15
Thanked 22 Times in 17 Posts
         
Re: OT - Electric Service in Garage

[ QUOTE ]
cant run a welder off 30amps, need 50 amps.

[/ QUOTE ]

Depending on the welder. Mine draws a max of about 70 running, but has a huge inrush when it turns on. Needs to be on a 150 amp breaker. Had it on a 100 amp breaker and it tripped it about half the times I turned it on.
Jim_Lou is offline  
post #6 of (permalink) Old 05-09-2005, 06:40 PM
Keyboard Implanted
 
JeepnGreg's Avatar
 
Join Date: Mar 2000
Location: Eureka IL
Posts: 4,676
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

sure ya can, just depends on the welders requirements

the Hobart 175 draws about 20 amps (i think) at its rated outputs

my garage is wired for 220v 30Amp breaker
JeepnGreg is offline  
post #7 of (permalink) Old 05-10-2005, 10:52 AM Thread Starter
Addict
 
westville's Avatar
 
Join Date: Apr 2001
Location: South Jersey
Posts: 410
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

Thanks. Any pref. of either the 8/3 or the roll of 8 wire and running 4 seperate wires?

The only thing I had left to buy was the wire. I have the dual 30A breaker. But, I only need 110 power.
westville is offline  
post #8 of (permalink) Old 05-10-2005, 10:58 AM
Keyboard Implanted
 
JeepnGreg's Avatar
 
Join Date: Mar 2000
Location: Eureka IL
Posts: 4,676
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

i have 4 seperate wires running in conduit.....i'll have to check what guage they are.

P.O. of the house did it
JeepnGreg is offline  
post #9 of (permalink) Old 05-10-2005, 11:10 AM
Moderator
 
Jim_Lou's Avatar
 
Join Date: Dec 2001
Location: Belleville, Illinois
Posts: 11,487
Thanks: 15
Thanked 22 Times in 17 Posts
         
Re: OT - Electric Service in Garage

Running conduit and pulling wires is the 'preferred' method, because later you can pull in bigger wires if you need to upgrade. On the other hand, a size larger wire is cheap. I'd go at least one size larger than I think I need, put in direct burial and be done with it. On the third hand, conduit will be less likely to be damaged when you bury the bodies. [img]/ubbthreads/images/graemlins/grin.gif[/img]
Jim_Lou is offline  
post #10 of (permalink) Old 05-10-2005, 11:15 AM Thread Starter
Addict
 
westville's Avatar
 
Join Date: Apr 2001
Location: South Jersey
Posts: 410
Thanks: 0
Thanked 0 Times in 0 Posts
 
Re: OT - Electric Service in Garage

All the books say 10ga for 30A and 8 for 40A. I know that 50 linear feet I will get a minimal voltage drop.

lom reccomended the 8 wire.

My house is so old, that this would be smallest issue when I go to sell it. My home was built in the 20s. The golden age of home building. Its so old that there was no plywood used in the construction of this house.

But, old things are cooler. That is why I bought it.
westville is offline  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Off-Road Forums & Discussion Groups forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Posting Rules  
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome